First time APC BACK-UPS user needs help with the Building wiring fault indicator
I bought a APC BACK-UPS RS 800VA 120V and love it! In the spring time
and early summer (believe it or not) I get a lot of power brownouts. The power company claims that squirrels are most of the cause of it (LOL). Anyway I carefully followed the instructions but still see the Building wiring fault indicator in red. I don't have three pronged outlets (old complex) so I grounded using the plate screw. Is this right? Should I be concerned? The unit runs perfectly though. I had an occurrence to see the APC in action a few days ago and my PC never batted a eye during the incident P.S. I used a two prong adaptor with an grounding wire. TIA |
#2
|
|||
|
|||
The UPS is also a surge suppressor. It will use the 3rd wire ground to route
any surges through. You probably don't have sufficient ground on the screw. Another thing that can cause the light to be on is high neutral voltage, a common problem in old buildings. The UPS part ought to work, the problem is going to be with the surge suppression. Also, there may be some other problem in the building wiring that could cause a problem for the entire building, depending on what it actually is. -- Wayne Morgan "Dunny Rummy" wrote in message ... I bought a APC BACK-UPS RS 800VA 120V and love it! In the spring time and early summer (believe it or not) I get a lot of power brownouts. The power company claims that squirrels are most of the cause of it (LOL). Anyway I carefully followed the instructions but still see the Building wiring fault indicator in red. I don't have three pronged outlets (old complex) so I grounded using the plate screw. Is this right? Should I be concerned? The unit runs perfectly though. I had an occurrence to see the APC in action a few days ago and my PC never batted a eye during the incident P.S. I used a two prong adaptor with an grounding wire. TIA |
#3
|
|||
|
|||
"Dunny Rummy" wrote in message
... I bought a APC BACK-UPS RS 800VA 120V and love it! In the spring time and early summer (believe it or not) I get a lot of power brownouts. The power company claims that squirrels are most of the cause of it (LOL). Anyway I carefully followed the instructions but still see the Building wiring fault indicator in red. I don't have three pronged outlets (old complex) so I grounded using the plate screw. Is this right? Should I be concerned? The unit runs perfectly though. I had an occurrence to see the APC in action a few days ago and my PC never batted a eye during the incident P.S. I used a two prong adaptor with an grounding wire. TIA If your UPS uses a single indicator to show problems it isn't going to be any help in determining what the problems might be. The best suggestion I can give is to buy one of the simple outlet testers sold at every hardware store and home center. These typically have three indicators on them and along with a chart will indicate exactly what is wrong. You should be prepared for the worst though -- the problem is likely to be something that requires at least opening and re-wiring your outlet(s) and/or it may require running new wires from the panel and providing a proper ground point. -- John McGaw [Knoxville, TN, USA] Return address will not work. Please reply in group or through my website: http://johnmcgaw.com |
#4
|
|||
|
|||
I rent in this apt complex
So rewiring might be out of the question. Maybe there is a way to run a ground wire but from where to where? The breaker box is just 2 feet from where the UPS is pluged in. A coworker said if I can find a water pipe I can run a wire from the water pipe to the outlet where the UPS is pluged in. Is this true? What am I looking for with this outlet tester? TIA On Tue, 13 Jan 2004 07:26:38 -0500, "John McGaw" wrote: "Dunny Rummy" wrote in message .. . I bought a APC BACK-UPS RS 800VA 120V and love it! In the spring time and early summer (believe it or not) I get a lot of power brownouts. The power company claims that squirrels are most of the cause of it (LOL). Anyway I carefully followed the instructions but still see the Building wiring fault indicator in red. I don't have three pronged outlets (old complex) so I grounded using the plate screw. Is this right? Should I be concerned? The unit runs perfectly though. I had an occurrence to see the APC in action a few days ago and my PC never batted a eye during the incident P.S. I used a two prong adaptor with an grounding wire. TIA If your UPS uses a single indicator to show problems it isn't going to be any help in determining what the problems might be. The best suggestion I can give is to buy one of the simple outlet testers sold at every hardware store and home center. These typically have three indicators on them and along with a chart will indicate exactly what is wrong. You should be prepared for the worst though -- the problem is likely to be something that requires at least opening and re-wiring your outlet(s) and/or it may require running new wires from the panel and providing a proper ground point. |
#5
|
|||
|
|||
"Dunny Rummy" wrote in message news I rent in this apt complex So rewiring might be out of the question. Maybe there is a way to run a ground wire but from where to where? The breaker box is just 2 feet from where the UPS is pluged in. A coworker said if I can find a water pipe I can run a wire from the water pipe to the outlet where the UPS is pluged in. Is this true? What am I looking for with this outlet tester? TIA It's possible the plug is not polarized correctly unplug it and flip it around. It the red light is still on then put it back the way it was as evidently there is a grounding propblem |
#6
|
|||
|
|||
|
#7
|
|||
|
|||
Is there a way to fix this if it is the problem?
I just want make sure my APC BACK-UPS will be able to carry out in the event of a black out or brownout. I get frustrated when I lose work when brownouts happen (though minnor). TIA! On Tue, 13 Jan 2004 09:14:28 -0600, "philo" wrote: "Dunny Rummy" wrote in message news I rent in this apt complex So rewiring might be out of the question. Maybe there is a way to run a ground wire but from where to where? The breaker box is just 2 feet from where the UPS is pluged in. A coworker said if I can find a water pipe I can run a wire from the water pipe to the outlet where the UPS is pluged in. Is this true? What am I looking for with this outlet tester? TIA It's possible the plug is not polarized correctly unplug it and flip it around. It the red light is still on then put it back the way it was as evidently there is a grounding propblem |
#8
|
|||
|
|||
"Dunny Rummy" wrote in message ... Is there a way to fix this if it is the problem? Yes! the outlet needs to be properly polarized and grounded. I just want make sure my APC BACK-UPS will be able to carry out in the event of a black out or brownout. I get frustrated when I lose work when brownouts happen (though minnor). TIA! If you use the UPS as it is presently...you may still have brownout protection... but there is definately a safety issue. Although you landlord *should* pay to have an electrician repair it... for the purpose of safety...maybe you could offer to pay half. It's a relatively minor job. |
#9
|
|||
|
|||
Safety ground is unrelated to battery backup - from
blackouts and brownouts. Most common failure of a UPS is dead battery. These plug-in UPSes tend to lose batteries in but a few years - rapid battery failure. Test is quite simple. Use computer with battery backup unplugged from wall receptacle. If computer works for many minutes, then battery inside battery backup is OK. That ground light does nothing for transient protection. In fact, that APC UPS does not even claim to protect from destructive transients. Read their specs (if even available). It claims no common mode transient protection; which is irrelevant to that red warning light. That red 'missing ground' light is reporting a human safety problem and a possible threat to interconnected electronics. Your receptacles are only two prong because no safety ground wire exists. Using the receptacle screw will do nothing because that safety ground wire is not installed. Only solution is to run a safety ground wire from breaker box. Even grounding to a cold water pipe is a bad and completely unacceptable solution; may create a threat to human safety; and not even sufficient as an earth ground. Note the difference - safety and earth grounds. That wall receptacle is missing a safety ground which is different from earth ground. Earth ground is necessary for transient protection. That red light can not report and does not even claim to test the existence of earth ground. That red light reports a human safety and other potential problems. Dunny Rummy wrote: Is there a way to fix this if it is the problem? I just want make sure my APC BACK-UPS will be able to carry out in the event of a black out or brownout. I get frustrated when I lose work when brownouts happen (though minnor). TIA! |
#10
|
|||
|
|||
w_tom wrote:
Safety ground is unrelated to battery backup - from blackouts and brownouts. Most common failure of a UPS is dead battery. These plug-in UPSes tend to lose batteries in but a few years - rapid battery failure. Test is quite simple. Use computer with battery backup unplugged from wall receptacle. If computer works for many minutes, then battery inside battery backup is OK. Speaking of UPSs, I have here a non-functional APC 420 Backup Pro that I picked up for $5 at a tag sale. I suspect it needs only a battery. Can I try it out with something like a car battery hooked in to check, and if it flies where does one go for a new internal battery? Meanwhile an APC BE350, which came from a Staples close-out at about $30, is doing fine. I also have old wiring with 2 pin plugs, so the power fault is always on. It gives me about 5 to 10 minutes to shut down. -- Chuck F ) ) Available for consulting/temporary embedded and systems. http://cbfalconer.home.att.net USE worldnet address! |
|
Thread Tools | |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Thread Starter | Forum | Replies | Last Post |
Monitor going back to 60 hz. | Helix | General | 1 | December 29th 03 05:01 PM |
2nd Hard Drive Disappears After Standby/hibernatio, Partition Magic Issue? | wrt | General | 1 | December 5th 03 08:20 PM |
PII vs PIII | Gregory L. Hansen | General | 114 | October 15th 03 05:56 PM |
P3-800 vs Celeron 1.4 --> video encoding time | PS | General | 15 | September 21st 03 06:14 PM |
See both TV and computer screen at SAME time? | Karl | General | 1 | July 14th 03 01:01 PM |