First time APC BACK-UPS user needs help with the Building wiring fault indicator



 
 
Thread Tools Display Modes
  #1  
Old January 13th 04, 09:19 AM
Dunny Rummy
external usenet poster
 
Posts: n/a
Default First time APC BACK-UPS user needs help with the Building wiring fault indicator

I bought a APC BACK-UPS RS 800VA 120V and love it! In the spring time
and early summer (believe it or not) I get a lot of power brownouts.
The power company claims that squirrels are most of the cause of it
(LOL).

Anyway I carefully followed the instructions but still see
the Building wiring fault indicator in red. I don't have three pronged
outlets (old complex) so I grounded using the plate screw. Is this
right? Should I be concerned? The unit runs perfectly though. I had an
occurrence to see the APC in action a few days ago and my PC never
batted a eye during the incident


P.S. I used a two prong adaptor with an grounding wire.

TIA
  #2  
Old January 13th 04, 11:27 AM
Wayne Morgan
external usenet poster
 
Posts: n/a
Default

The UPS is also a surge suppressor. It will use the 3rd wire ground to route
any surges through. You probably don't have sufficient ground on the screw.
Another thing that can cause the light to be on is high neutral voltage, a
common problem in old buildings. The UPS part ought to work, the problem is
going to be with the surge suppression. Also, there may be some other
problem in the building wiring that could cause a problem for the entire
building, depending on what it actually is.

--
Wayne Morgan


"Dunny Rummy" wrote in message
...
I bought a APC BACK-UPS RS 800VA 120V and love it! In the spring time
and early summer (believe it or not) I get a lot of power brownouts.
The power company claims that squirrels are most of the cause of it
(LOL).

Anyway I carefully followed the instructions but still see
the Building wiring fault indicator in red. I don't have three pronged
outlets (old complex) so I grounded using the plate screw. Is this
right? Should I be concerned? The unit runs perfectly though. I had an
occurrence to see the APC in action a few days ago and my PC never
batted a eye during the incident


P.S. I used a two prong adaptor with an grounding wire.

TIA



  #3  
Old January 13th 04, 12:26 PM
John McGaw
external usenet poster
 
Posts: n/a
Default

"Dunny Rummy" wrote in message
...
I bought a APC BACK-UPS RS 800VA 120V and love it! In the spring time
and early summer (believe it or not) I get a lot of power brownouts.
The power company claims that squirrels are most of the cause of it
(LOL).

Anyway I carefully followed the instructions but still see
the Building wiring fault indicator in red. I don't have three pronged
outlets (old complex) so I grounded using the plate screw. Is this
right? Should I be concerned? The unit runs perfectly though. I had an
occurrence to see the APC in action a few days ago and my PC never
batted a eye during the incident


P.S. I used a two prong adaptor with an grounding wire.

TIA


If your UPS uses a single indicator to show problems it isn't going to be
any help in determining what the problems might be. The best suggestion I
can give is to buy one of the simple outlet testers sold at every hardware
store and home center. These typically have three indicators on them and
along with a chart will indicate exactly what is wrong. You should be
prepared for the worst though -- the problem is likely to be something that
requires at least opening and re-wiring your outlet(s) and/or it may require
running new wires from the panel and providing a proper ground point.
--
John McGaw
[Knoxville, TN, USA]

Return address will not work. Please
reply in group or through my website:
http://johnmcgaw.com

  #4  
Old January 13th 04, 02:26 PM
Dunny Rummy
external usenet poster
 
Posts: n/a
Default

I rent in this apt complex
So rewiring might be out of the question. Maybe there is a way to run
a ground wire but from where to where?
The breaker box is just 2 feet from where the UPS is pluged in. A
coworker said if I can find a water pipe I can run a wire from the
water pipe to the outlet where the UPS is pluged in. Is this true?
What am I looking for with this outlet tester?
TIA


On Tue, 13 Jan 2004 07:26:38 -0500, "John McGaw"
wrote:

"Dunny Rummy" wrote in message
.. .
I bought a APC BACK-UPS RS 800VA 120V and love it! In the spring time
and early summer (believe it or not) I get a lot of power brownouts.
The power company claims that squirrels are most of the cause of it
(LOL).

Anyway I carefully followed the instructions but still see
the Building wiring fault indicator in red. I don't have three pronged
outlets (old complex) so I grounded using the plate screw. Is this
right? Should I be concerned? The unit runs perfectly though. I had an
occurrence to see the APC in action a few days ago and my PC never
batted a eye during the incident


P.S. I used a two prong adaptor with an grounding wire.

TIA


If your UPS uses a single indicator to show problems it isn't going to be
any help in determining what the problems might be. The best suggestion I
can give is to buy one of the simple outlet testers sold at every hardware
store and home center. These typically have three indicators on them and
along with a chart will indicate exactly what is wrong. You should be
prepared for the worst though -- the problem is likely to be something that
requires at least opening and re-wiring your outlet(s) and/or it may require
running new wires from the panel and providing a proper ground point.


  #5  
Old January 13th 04, 03:14 PM
philo
external usenet poster
 
Posts: n/a
Default


"Dunny Rummy" wrote in message
news
I rent in this apt complex
So rewiring might be out of the question. Maybe there is a way to run
a ground wire but from where to where?
The breaker box is just 2 feet from where the UPS is pluged in. A
coworker said if I can find a water pipe I can run a wire from the
water pipe to the outlet where the UPS is pluged in. Is this true?
What am I looking for with this outlet tester?
TIA



It's possible the plug is not polarized correctly
unplug it and flip it around. It the red light is still on then put it back
the way it was as evidently there is a grounding propblem


  #6  
Old January 13th 04, 03:19 PM
ChrisJ9876
external usenet poster
 
Posts: n/a
Default

From: "Wayne Morgan"
Date: 01/13/2004 6:27 AM Eastern Standard Time
Message-id:

The UPS is also a surge suppressor. It will use the 3rd wire ground to route
any surges through. You probably don't have sufficient ground on the screw.
Another thing that can cause the light to be on is high neutral voltage, a
common problem in old buildings. The UPS part ought to work, the problem is
going to be with the surge suppression. Also, there may be some other
problem in the building wiring that could cause a problem for the entire
building, depending on what it actually is.

--
Wayne Morgan


"Dunny Rummy" wrote in message
.. .
I bought a APC BACK-UPS RS 800VA 120V and love it! In the spring time
and early summer (believe it or not) I get a lot of power brownouts.
The power company claims that squirrels are most of the cause of it
(LOL).

Anyway I carefully followed the instructions but still see
the Building wiring fault indicator in red. I don't have three pronged
outlets (old complex) so I grounded using the plate screw. Is this
right? Should I be concerned? The unit runs perfectly though. I had an
occurrence to see the APC in action a few days ago and my PC never
batted a eye during the incident


P.S. I used a two prong adaptor with an grounding wire.

TIA




If it's an old building with old wiring, it's possible that the outlet box is
not grounded at all; if so, the wire you attached to the plate screw is not
connected to ground.
  #7  
Old January 13th 04, 04:04 PM
Dunny Rummy
external usenet poster
 
Posts: n/a
Default

Is there a way to fix this if it is the problem?
I just want make sure my APC BACK-UPS will be able to carry out in the
event of a black out or brownout. I get frustrated when I lose work
when brownouts happen (though minnor).
TIA!


On Tue, 13 Jan 2004 09:14:28 -0600, "philo" wrote:


"Dunny Rummy" wrote in message
news
I rent in this apt complex
So rewiring might be out of the question. Maybe there is a way to run
a ground wire but from where to where?
The breaker box is just 2 feet from where the UPS is pluged in. A
coworker said if I can find a water pipe I can run a wire from the
water pipe to the outlet where the UPS is pluged in. Is this true?
What am I looking for with this outlet tester?
TIA



It's possible the plug is not polarized correctly
unplug it and flip it around. It the red light is still on then put it back
the way it was as evidently there is a grounding propblem


  #8  
Old January 13th 04, 08:07 PM
philo
external usenet poster
 
Posts: n/a
Default


"Dunny Rummy" wrote in message
...
Is there a way to fix this if it is the problem?


Yes! the outlet needs to be properly polarized and grounded.

I just want make sure my APC BACK-UPS will be able to carry out in the
event of a black out or brownout. I get frustrated when I lose work
when brownouts happen (though minnor).
TIA!



If you use the UPS as it is presently...you may still have brownout
protection...
but there is definately a safety issue.

Although you landlord *should* pay to have an electrician repair it...
for the purpose of safety...maybe you could offer to pay half. It's a
relatively
minor job.


  #9  
Old January 14th 04, 02:27 PM
w_tom
external usenet poster
 
Posts: n/a
Default

Safety ground is unrelated to battery backup - from
blackouts and brownouts. Most common failure of a UPS is dead
battery. These plug-in UPSes tend to lose batteries in but a
few years - rapid battery failure. Test is quite simple. Use
computer with battery backup unplugged from wall receptacle.
If computer works for many minutes, then battery inside
battery backup is OK.

That ground light does nothing for transient protection. In
fact, that APC UPS does not even claim to protect from
destructive transients. Read their specs (if even
available). It claims no common mode transient protection;
which is irrelevant to that red warning light.

That red 'missing ground' light is reporting a human safety
problem and a possible threat to interconnected electronics.
Your receptacles are only two prong because no safety ground
wire exists. Using the receptacle screw will do nothing
because that safety ground wire is not installed. Only
solution is to run a safety ground wire from breaker box.
Even grounding to a cold water pipe is a bad and completely
unacceptable solution; may create a threat to human safety;
and not even sufficient as an earth ground.

Note the difference - safety and earth grounds. That wall
receptacle is missing a safety ground which is different from
earth ground. Earth ground is necessary for transient
protection. That red light can not report and does not even
claim to test the existence of earth ground. That red light
reports a human safety and other potential problems.

Dunny Rummy wrote:
Is there a way to fix this if it is the problem?
I just want make sure my APC BACK-UPS will be able to carry out in the
event of a black out or brownout. I get frustrated when I lose work
when brownouts happen (though minnor).
TIA!

  #10  
Old January 14th 04, 07:34 PM
CBFalconer
external usenet poster
 
Posts: n/a
Default

w_tom wrote:

Safety ground is unrelated to battery backup - from
blackouts and brownouts. Most common failure of a UPS is dead
battery. These plug-in UPSes tend to lose batteries in but a
few years - rapid battery failure. Test is quite simple. Use
computer with battery backup unplugged from wall receptacle.
If computer works for many minutes, then battery inside
battery backup is OK.


Speaking of UPSs, I have here a non-functional APC 420 Backup Pro
that I picked up for $5 at a tag sale. I suspect it needs only a
battery. Can I try it out with something like a car battery
hooked in to check, and if it flies where does one go for a new
internal battery?

Meanwhile an APC BE350, which came from a Staples close-out at
about $30, is doing fine. I also have old wiring with 2 pin
plugs, so the power fault is always on. It gives me about 5 to 10
minutes to shut down.

--
Chuck F ) )
Available for consulting/temporary embedded and systems.
http://cbfalconer.home.att.net USE worldnet address!


 




Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

vB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Threads
Thread Thread Starter Forum Replies Last Post
Monitor going back to 60 hz. Helix General 1 December 29th 03 05:01 PM
2nd Hard Drive Disappears After Standby/hibernatio, Partition Magic Issue? wrt General 1 December 5th 03 08:20 PM
PII vs PIII Gregory L. Hansen General 114 October 15th 03 05:56 PM
P3-800 vs Celeron 1.4 --> video encoding time PS General 15 September 21st 03 06:14 PM
See both TV and computer screen at SAME time? Karl General 1 July 14th 03 01:01 PM


All times are GMT +1. The time now is 05:08 PM.


Powered by vBulletin® Version 3.6.4
Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 HardwareBanter.
The comments are property of their posters.